Jump directly to main navigation Jump directly to content

Details on the Calculation Dialog for Open Drainage

Information on the dialog LINEAR Analyse Waste Water - Open drainage.

The calculation dialog shows an overview of the detected pipe network and contains all functions necessary for the calculation.

You are here:

Project tabDiscipline Waste Water Analyse tabCalculation

Analyse Waste Water calculation Linear Revit

Functions for the calculation

The functions in the upper part of the calculation dialog pertain to the entire pipe network.

Element

Meaning

Systems

If the project contains several systems or partial networks you may determine which of the systems or partial network to display in the calculation dialog’s tables.

This button will open the technical data of the initial component. Here, you can change the system name shown in the drop-down list.

Calculate

Initiate the calculation of the pipe network after having made changes to see current calculation results.

Visualization ...

This function displays properties and calculation results of the pipe network in color in the model.

Results...

Displays additional information regarding the pipe network and an overview of the calculation results, which also are part of the printouts.

Reports ...

Displays an overview of notes, warnings and errors that occurred during calculation. You can recognize the type of report by the color of the button:

green check mark: No current notes, warnings or errors.

blue i There are notes on the calculation.

yellow warning triangle: There are warnings for the calculation.

red cross: There are errors in the calculation.

Note:

Please always read the report very carefully to correct the errors contained in the model and to ensure a correct calculation of your pipe network.

Labeling ...

Label components and duct sections with calculation results.

Update <

If components or duct sections have already been labeled and calculation results have changed retrospectively, this button will refresh all labels with current data.

Functions of the tables

In sections Flow paths, Pipe sections and Ventilated by pipe section(s) similar functions are presented.

Element

Description

Maximize list

The tables of flow paths, duct sections and ventilation duct sections can be enlarged over the entire calculation dialog. The other tables are hidden.

Minimize list

This function minimizes a maximized table. The other tables are displayed again.

Search <

This function is available in sections Flow paths, Pipe sections and Ventilated by. After clicking Search < select the element in the model. The respective table then shows the flow path, the pipe section or the ventilation duct section.

If a certain flow path number, a pipe section number or a ventilation duct section number needs to be found, enter the number into the text field and click Search <. The respective table then shows the flow path, the pipe section or the ventilation duct section.

Show

This function is available in sections Flow paths, Pipe sections and Ventilated by. First, select the element from the table and click Show. The flow path, the pipe section or the ventilation duct section is shown in the model.

Edit...

This function is available in sections Flow paths, Pipe sections and Ventilated by. First, select the element in the table and click Edit.... The dialog for editing drainage element, pipe section or ventilation duct section is opened.

Edit <

This function is available in sections Pipe section, and Ventilated by. After clicking Edit in drawing, select the element in the model. The dialog for editing pipe sections is opened.

Edit component data via drawing <

This function is available in section Ventilated by. Select the component in your model after clicking edit via drawing <. The dialog for editing the component is opened.

Table for flow paths

This table shows the calculation data for all flow paths of the selected system. It provides an overview over all ending components of the network. If you select a flow path, the table Pipe sections displays all corresponding pipe sections. The most unfavorable flow path is highlighted in a different color. You can also select the most unfavorable flow path by pressing U.

Column

Description

(without title)

Pipe type:

S: Sewage water

R: Rain water

No.

Flow path number.

Name

Name of the drainage element.

DU

Connection value

Qc

Water inflow.

A

Connected roof area.

Qr

Rainwater outflow rate.

C

Discharge coefficient.

DN

Dimensioning target.

Table for pipe sections

This table shows the calculation data for all pipe sections of the selected flow path. If you select a pipe section, the table Ventilated via pipe section(s) displays all corresponding ventilation pipe sections.

Apply pipe section data globally

Opens the dialog Define pipe sections. This function allows you to assign or reset certain properties of selected or all pipe sections.

Unfix / fix pipe sections

This function allows you to fix or unfix the dimensions of all pipe sections. If values are displayed in bold in the DN column, the dimension of the respective pipe sections will not be adjusted during the calculation. This is sensible when calculating existing systems. If the dimensions of some pipe sections have been fixed already, you will be asked whether to fix or unfix all pipe sections.

Column

Description

(without title)

Pipe type:

S: Sewage water

R: Rain water

M: Mixed water

No.

Number of the duct section.

Type

DP: Down pipe

G: Ground pipe

ColP: Collector pipe

S: Collecting pipe

SCP: Single connector pipe

(i): inside the building

(o): outside the building

Pipe type can be changed in the table.

L

The length of the pipe section determined in accordance with the norm, taking into account all relevant fittings. The length be changed in the table. The new length will be distributed among all ducts of the duct sections proportionately to constructed length. All pipes affected by the change in length will be displayed bold in the tables for duct sections and components.

H

Height of pipe section.

U

Number of individuals ( if calculated according to SP 30.13330.2016 and SP 30.13330.2020)

N

Number of sanitary ( if calculated according to SP 30.13330.2016 and SP 30.13330.2020)

P

Probability of use ( if calculated according to SP 30.13330.2016 and SP 30.13330.2020).

NP

Product of the number of sanitary objects and the probability of use ( if calculated according to SP 30.13330.2016 and SP 30.13330.2020).

α

Simultaneity factor ( if calculated according to SP 30.13330.2016 and SP 30.13330.2020)

DN

Nominal diameter of pipes in this pipe section. The nominal diameter can be changed in the table. The value is then fixed and will not be adjusted by the software during calculation. Fixed values are shown in bold.

DU

Connection value.

Qww

Waste water discharge.

Qp

Pump flow rate, if a pump exists.

Qc

Continuous flow rate.

Qtot

Total waste water discharge.

A

Connected roof area.

Qr

Rainwater outflow rate.

Qm

Mixed water outflow.

J

Slope. The slope can be changed in the table.

h/d

Filling degree. The tooltip in this field shows the actual- and max-condition of the current loads.

w

Flow velocity in collecting- and ground pipes.

Table Ventilated by pipe section(s)

This table shows the calculation data for all ventilation duct sections of the selected pipe section.

Lock/unlock pipe sections

This function allows you to fix or unfix the dimensions of all pipe sections. The column NPS displays all values in bold and pipe section dimensions are not adjusted during calculation. This is sensible when calculating existing systems. A repeated click on this button unfixes all dimensions. If the dimensions of some pipe sections have been fixed already, you will be asked whether to fix or unfix all pipe sections.

Column

Description

(without title)

Pipe type:

L: Ventilating pipe

No.

Number of the ventilating pipe.

Type

Type of ventilation pipe. The ventilation pipe can be changed in the table.

L

The length of the pipe section determined in accordance with the norm, taking into account all relevant fittings. The length be changed in the table. The new length will be distributed among all ducts of the duct sections proportionately to constructed length. All pipes affected by the change in length will be displayed bold in the tables for duct sections and components.

H

Height of pipe section.

DN

Nominal diameter of pipes in this pipe section. The nominal diameter can be changed in the table. The value is then fixed and will not be adjusted by the software during calculation. Fixed values are shown in bold.

Adjusting nominal diameters

If calculated nominal diameters deviate from those constructed, calculated nominal diameters can be transferred into the model. You can adjust the nominal diameters for the entire network or for partial networks.