Details on the Heating and Cooling Calculation Dialog

Information about the LINEAR Analyse Heating and LINEAR Analyse Cooling dialogs.

The calculation dialog shows an overview of the detected pipe network and contains all commands necessary for the calculation.

You are here:

Project tabDiscipline heatingPlanning typeAnalyse tabCalculation ...

Applies to: Heating and Cooling.

Dialog calculation Linear

Commands for the calculation

The commands in the upper part of the calculation dialog pertain to the entire pipe network.

Element

Meaning

Systems

If the project contains several systems or partial networks you may determine which of the systems or partial network to display in the calculation dialog’s tables.

This button will open the technical data of the initial component. Here, you can change the system name shown in the drop-down list.

Calculate

Initiate the calculation of the pipe network after having made changes to see current calculation results.

Visualization ...

This command displays properties and calculation results of the pipe network in color in the drawing.

Results ...

Displays additional information regarding the pipe network and an overview of the calculation results, which also are part of the printouts.

Reports ...

Displays an overview of notes, warnings and errors that occurred during calculation. You can recognize the type of report by the color of the button:

green check mark: No current notes, warnings or errors.

blue i There are notes on the calculation.

yellow warning triangle: There are warnings for the calculation.

red cross: There are errors in the calculation.

Note:

It is recommended to always carefully read the reports to correct errors in the drawing and ensure a proper calculation of the pipe network.

Basic conditions

Opens the dialog Basic conditions, which allows you to change basic calculation-parameters like specifications for hydraulic balancing, upper limits for max. velocities, max. pipe friction pressure gradient as well as settings for the dimensioning of thermostatic valves, regulating valves and differential pressure closed-loop controllers.

Labeling ...

Label components and duct sections with calculation results.

Update <

If components or duct sections have already been labeled and calculation results have changed retrospectively, this button will refresh all labels with current data.

Commands for the tables

Similar commands are available in the Flow paths, Pipe sections and Componentssections.

Element

Description

Search <

The command is available in the Flow paths, Pipe sections and Components sections. After clicking Search < select the element in the drawing. The respective table then highlights the flow path, the pipe section or the component.

If a certain flow path number, a pipe section number or a component number needs to be found, enter the number into the text field and click Search <. The respective table then highlights the flow path, the pipe section or the component.

Show

The command is available in the Flow paths, Pipe sections and Components sections. First, select the element from the table and click Show. The flow path, the pipe section or the component is shown in the drawing.

Edit...

The command is available in the Flow paths, Pipe sections and Components sections. First, select the element in the table and click Edit.... The dialog for editing components or duct sections is opened.

Edit <

The command is available in the Duct section, and Components sections. After clicking edit in drawing <, select the element in the drawing. The dialog for editing components or duct sections is opened.

Table for flow paths

This table shows the calculation data for all flow paths of the selected system. It provides an overview over all ending components of the network. If you select a flow path, the table Pipe sections displays all corresponding pipe sections. The most unfavorable flow path is highlighted in a different color. You can also select the most unfavorable flow path by pressing U.

Pressure loss

Opens the dialog Flow path data in which pressure losses over the course of a flow path are shown in a graph.

Column

Description

No.

Flow path number.

Name

Name of the heat- or chill consumer.

L

Length of the flow path. Changes for length in the tables pipe/duct sections and components take effect after the next calculation.

m

Mass flow rate of the heat- or chill consumer. The tooltip shows the component number and the power output of the consumer.

dpPipe

Pressure loss due to pipe friction.

dpFit

Pressure loss due to fittings (e. g. bends, t-pieces, reducing parts, transitions, manifolds).

dpValve

Pressure loss due to valves from Kv value (e. g. fixed resistors, shut-off valve).

dpConst

Constant pressure losses due to manually entered values (e. g. for radiators, heat exchanger).

dpContr

Pressure loss through 3-way control valves.

dpThrot

Pressure loss due to throttling valves (e. g. throttle valve, regulating valves).

dpTot

Pressure loss for the entire flow path.

dpPmp

Total pressure loss in flow path overcome by the pump. The tooltip displays the number of pumps.

Table for pipe sections

This table shows the calculation data for all pipe sections of the selected flow path. If you select a duct section, the table Components displays all corresponding components.

Built-in parts or fittings can be classified as section separators

This function allows you to classify fittings or built-in parts in the pipe network as separating elements for pipe sections, e.g. in order to assign different pipe material or to create clear separations for the automatic assignment of material.

Apply pipe section data globally

Opens the dialog Define pipe sections. This command allows you to assign or reset certain properties of selected or all pipe sections at the same time.

Unfix / fix pipe sections

This command allows you to fix or unfix the dimensions of all pipe sections. If values are displayed in bold in theDN column, the dimension of the respective pipe sections will not be adjusted during the calculation. This is sensible when calculating existing systems. If the dimensions of some pipe sections have been fixed already, you will be asked whether to fix or unfix all pipe sections.

Column

Description

No.

Number of the duct section.

Type

HSW: Supply water

HRW: Return water

SWHC: Supply water Heating/Cooling

RWHC: Return water Heating/Cooling

L

Length of pipe section. The length be changed in the table. The new length will be distributed among all ducts of the duct sections proportionately to constructed length. All pipes affected by the change in length will be displayed bold in the tables for duct sections and components.

Q

Heat flow rate of this pipe/duct section. The tooltip shows the simultaneity and the resulting heat flow rate.

m

Mass flow rate in this pipe/duct section. The tooltip shows the simultaneity and the resulting heat flow rate.

DN

Nominal diameter of pipes in this pipe section. The nominal diameter can be changed in the table. The value is then fixed and will not be adjusted by the software during calculation. Fixed values are shown in bold.

T

Design operating temperature. The tooltip shows the operating temperature, the ambient temperature and the specific heat loss.

w

Mean flow velocity in this pipe/duct section.

R

R-value in pipes.

dpR

Pressure loss due to pipe friction.

Sum zeta

Sum of zeta values in this pipe section.

dpZ

Pressure loss due to zeta value.

dpA

Pressure losses of adjustable appliances and valves.

dpTot

Sum pressure loss of this pipe section.

Table for components

The table shows the calculation data of all components contained in the selected pipe section.

Column

Description

No.

Component number.

Name

Name of the component.

m

Mass flow rate of this component.

L

For pipes: Length. The length be changed in the table. The new length will be used in all pipe sections containing the respective pipe. All pipes affected by the change in length will be displayed bold in the tables for duct sections and components.

DN

Dimension.

VAR: Dimension varies.

Zeta

Zeta value of component.

dpZ

Pressure loss of this built-in part.

Kv

Flow coefficient.

dpKv

Pressure loss due to Cv value.

dpPipe

Pressure loss of this pipe.

dpA

Pressure loss by appliances.

dpTot

Total pressure loss of this component.

Generating 3D pipes

Allows the assignment of pipe materials from the 3D Piping module after the calculation of a single-line pipe - network. After successful assignment, a three-dimensional pipe network is generated. Pre-assigned insulation material is considered. This process requires a license for the LINEAR 3D Design Pipe&Power module.

Note:

Make a backup copy of your drawing before having the 1-line pipe network converted to 3D.

The result of 3D generation may vary depending on which pipe material was chosen. It may occur that calculated nominal pipe sizes are not available for the selected 3D pipe material. This can lead to deviating results or open ends when calculating the 3D pipe network.