Details on Ventilation
Information about the Ventilation section in the general heat load data.
You are here:
Drop-down list: Selection of the ventilation system
Select the type of ventilation system as the default setting for the project. This default setting is initially adopted for each ventilation zone. You can make a different specification in each ventilation zone. The selection of ventilation systems is based on the Ventilation module. If the Ventilation module is activated, the settings between the two modules are automatically synchronized. If you change the settings and different settings were made in ventilation zones or rooms, you will be asked whether the new setting should be applied to all rooms. If different ventilation systems are selected in the individual rooms, the display of the ventilation system at project level (general heat load data) depends on which system is most frequently used in the rooms.
Eta value (heat recovery)
Enter the efficiency of the heat recovery system in percent. It is only used if a supply and extract air system is available. The efficiency is then used to calculate the supply air temperature of supply air rooms.
Design pressure difference of the OuAO
Specify here the design pressure difference with which outside air diffusers are dimensioned in the ventilation concept.