Details on Technical Data for Hydrants

Information on the technical data dialog for Hydrants.

A hydrant can be place and connected like a component (WC, wash stand, etc.).

You are here:

Project tabDisciplineAnalyse tabComponentsTechnical dataComponent

Attention:

According to DIN 1988-6, within a potable water system, only hydrants are permitted as self-support devices.

They must be defined with a calculation flow rate of a maximum of 2 x 24 l/min with a minimum flow pressure of 2000 hPa. Wall hydrants are to be installed with a securing combination. This combination is made up of a backflow prevention mechanism and pipe ventilation. The drawn pipe should be kept as short as possible. In the event of a greater firefighting water requirement, a separate firefighting network should be planned.

Name

Specifies the name of the component. You can modify the name. Clicking restores the default setting.

Consideration

Use the drop-down list to specify how the hydrant should be included in the calculation.

Option

Description

Consider minimum flow pressure.

The geodetic pressure loss is calculated up to the hydrant.

Consideration of minimum flow pressure and fire water flow rate

Allows you to consider not only the minimum flow pressure but also the fire water flow rate in the design.

do not consider

The hydrant is not included in the calculation.

Minimum flow pressure: Enter the minimum flow pressure in hPa. The consumers are generally predefined with expedient values.

Flow rate fire water: In case of Consideration of minimum flow pressure and fire water flow rate, specify the fire water flow rate to be considered in the dimensioning in l/s.

Min. nominal diameter: In this field you define the minimum size of the wall hydrant. In the calculation, it is thus not possible to select a smaller dimension.

Reset: If you changed the values manually, you can use the Reset button to reset the values to the default data.